Refer to the partial drawing of two identical centrifugal pumps in a cooling water system ___

Refer to the partial drawing of two identical centrifugal pumps in a cooling water system (see figure below).

two identical radial-flow centrifugal pumps - PG-7

Each pump is driven by an identical three-phase AC induction motor.

The cooling water system is being returned to service following maintenance on the pumps.

Pump A was started five minutes ago to initiate flow in the cooling water system.

Pump B is about to be started.

When pump B is started, which one of the following will cause pump B to experience high starting current for a shorter time than usual before stabilizing at a lower running current?

A. Pump B is initially rotating in the reverse direction.
B. The motor coupling for pump B was removed and not reinstalled.
C. The packing gland for pump B was tightened since the pump last operated.
D. The voltage applied to the motor for pump B is 20 percent lower than normal.

Show Answer

Answer: B

Share your understanding of this question with the correct explanation.