The Radial System distribution system, as shown, requires both relays to have ___

The Radial System distribution system, as shown, requires both relays to have a Standard Inverse (SI) operation curve according to IEC 60255.

If the relay at Bus B is set to be done Work as a backup protection for the relay at Bus A, with a margin of time = 0.35 seconds.

Ask how much TMS of the relay B must be adjusted at Bus B

A. TMS of relay at Bus B = 0.176
B. TMS of relay at Bus B = 0.078
C. TMS of relay at Bus B = 0.095
D. TMS of relay at Bus B = 0.35

Show Answer

Answer: B

Share your understanding of this question with the correct explanation.