Two identical 1,000 MW generators are operating in parallel, supplying all the loads on an isolated electrical bus ___

Two identical 1,000 MW generators are operating in parallel, supplying all the loads on an isolated electrical bus.

The generator output breakers provide identical protection for the generators.

Generator A and B output indications are as follows:

Generator-PG-53

A malfunction causes the voltage regulator setpoint for generator B to slowly and continuously decrease.

If no operator action is taken, the electrical current indication for generator B will…

A. initially decrease, and then increase until the output breaker for generator A trips on overcurrent.

B. initially decrease, and then increase until the output breaker for generator B trips on overcurrent.

C. decrease continuously until the output breaker for generator A trips on overcurrent.

D. decrease continuously until the output breaker for generator B trips on reverse power.

Show Answer

Answer: A

Share your understanding of this question with the correct explanation.