What is Live Zero in 4-20 mA?

:high_voltage: What is Live Zero in 4–20 mA?

One of the smartest features of the 4–20 mA signal is something called Live Zero :backhand_index_pointing_down:


:gear: What is Live Zero?

:right_arrow: In a 4–20 mA loop:

:small_blue_diamond: 4 mA = 0% Process Value
:small_blue_diamond: 20 mA = 100% Process Value

Even when the measured value is zero, the transmitter still sends 4 mA, not 0 mA.

:backhand_index_pointing_right: This is called Live Zero.


:brain: Why not use 0–20 mA?

Because with 0–20 mA:

:red_question_mark: Is 0 mA a valid measurement?
:red_question_mark: Or is the wire broken?

You cannot tell the difference.


:rocket: Advantage of Live Zero

With 4–20 mA:

:green_circle: 4 mA = Valid process value (0%)
:red_circle: 0 mA = Fault condition

This makes fault detection easy.


:bar_chart: Example

Pressure Range = 0–100 bar

:small_blue_diamond: 4 mA → 0 bar
:small_blue_diamond: 12 mA → 50 bar
:small_blue_diamond: 20 mA → 100 bar

If PLC reads:

:police_car_light: 0 mA → Wire break / power loss
:police_car_light: 2 mA → Loop fault or transmitter issue


:factory: Why industries love Live Zero

:high_voltage: Detects open-circuit faults
:high_voltage: Detects transmitter power loss
:high_voltage: Improves troubleshooting
:high_voltage: Increases system reliability


:warning: Common alarm settings

Many PLCs/DCS systems use:

:red_circle: < 3.6 mA → Under-range / Fault
:red_circle: > 21 mA → Over-range / Fault

(As per NAMUR NE43 recommendations)


:bullseye: Key takeaway

:backhand_index_pointing_right: 4 mA is not “zero current”
:backhand_index_pointing_right: 4 mA means “I am alive and measuring zero”


:light_bulb: Simple understanding

Live Zero = The transmitter sends 4 mA at zero measurement so the control system knows the instrument is healthy and the wiring is intact.

Video Tutorial:


#Instrumentation #420mA #LiveZero #ProcessControl #PLC dcs #IndustrialAutomation #Engineering #ProcessInstrumentation Automation :rocket: