Which RTD is less affected by lead wire resistance?

Which RTD is less affected by lead wire resistance?

A. Pt10
B. Pt500
C. Pt100
D. Pt1000

View Answer

Answer: D

Explanation:

Pt1000 RTDs are less affected by lead wire resistance because their base resistance is much higher than that of other RTD types.

At 0°C:

  • Pt10 = 10 Ω
  • Pt100 = 100 Ω
  • Pt500 = 500 Ω
  • Pt1000 = 1000 Ω

Consider a lead wire resistance of 2 Ω:

For a Pt100

Error percentage:

(2 ÷ 100) × 100 = 2%

For a Pt1000

Error percentage:

(2 ÷ 1000) × 100 = 0.2%

The same lead wire resistance produces a much smaller measurement error in a Pt1000 because the sensor’s resistance is higher.

Why Pt1000 Performs Better

:white_check_mark: Lower percentage error from cable resistance
:white_check_mark: Better signal-to-noise ratio
:white_check_mark: Improved accuracy in 2-wire installations
:white_check_mark: Suitable for long cable runs

Although 3-wire and 4-wire configurations are commonly used to compensate for lead resistance, among the RTD types listed, Pt1000 is inherently the least affected by lead wire resistance.

Therefore, Option D (Pt1000) is the correct answer. :white_check_mark: