Hello,
How can I convert 4-20mA to 0-20mA in tiaportal?
Hello,
How can I convert 4-20mA to 0-20mA in tiaportal?
Go to Devices & Networks
Select your PLC (S7-1200 / S7-1500)
Click the analog module (AI card)
Click on the module
In the right panel, select the channel (AI0 / AI1 / …)
Under “Properties” → “Channel” → “Measuring Type”
You will see options like:
4…20 mA
0…20 mA
±20 mA
Voltage ranges (0–10 V, ±10 V, etc.)
Select:
This tells the card to treat 0 mA as minimum instead of 4 mA.
After setting 0–20 mA, press:
Compile
Download to device
Put CPU in RUN
Now your analog input will interpret 0–20 mA correctly.
After setting 0–20 mA, the Siemens raw values change:
So you get:
| Current | Raw Value |
|---|---|
| 0 mA | 0 |
| 10 mA | ~13824 |
| 20 mA | 27648 |
No scaling offset is needed.