A Quick Summary of 4-20 mA Conversion Formulas

4–20 mA conversions are one of those “small” skills that quietly drive everything:
Calibration. Loop checks. PLC/DCS scaling. Troubleshooting weird readings.

If you can convert between PV, % span and mA in your sleep, everything else in a control loop gets easier.

4-20 mA Conversion Formulas







In this carousel, I used one simple example:

Pressure transmitter
LRV = 0 bar, URV = 10 bar → Span = 10 bar

Then ran it through 7 common formula types using the same numbers:
PV = 7.5 bar and mA = 12.0 mA

  1. Span
    Span = URV − LRV = 10 − 0 = 10 bar

  2. %Span from PV
    % = (PV − LRV)/Span × 100 = (7.5 − 0)/10 × 100 = 75%

  3. mA from %Span
    mA = 4 + (%/100) × 16 = 4 + 0.75 × 16 = 16 mA

  4. %Span from mA
    % = (mA − 4)/16 × 100 = (12 − 4)/16 × 100 = 50%

  5. PV from mA
    PV = LRV + (mA − 4)/16 × Span = 0 + 8/16 × 10 = 5 bar

  6. PV from %Span
    PV = LRV + (%/100) × Span = 0 + 0.5 × 10 = 5 bar

  7. mA from PV (direct)
    mA = 4 + (PV − LRV)/Span × 16 = 4 + 7.5/10 × 16 = 16 mA