✅ Calculation & Calibration of Pressure Transmitter (4–20 mA Loop)

Calculation & Calibration of Pressure Transmitter (4–20 mA Loop)

:small_blue_diamond: Important Definitions

1. URL (Upper Range Limit)

The highest value of the calibrated measurement range that the transmitter can measure.

2. LRL (Lower Range Limit)

The lowest value of the calibrated measurement range that the transmitter can measure.

3. LRV (Lower Range Value)

The process value corresponding to the LRL, representing 0% of span.

4. URV (Upper Range Value)

The process value corresponding to the URL, representing 100% of span.


:pushpin: Example – Pressure Transmitter (0–20 psi)

Parameter Value
LRL 0 psi
LRV 0 psi
URL 20 psi
URV 20 psi

Span = URL − LRL = 20 − 0 = 20 psi


:white_check_mark: Pressure Calculation When 4–20 mA is Given

Given:

  • Current range = 4–20 mA

  • Pressure range = 0–20 bar


:one: Calculate the Span

  • Pressure span = 20 − 0 = 20 bar

  • Current span = 20 − 4 = 16 mA


:two: Scaling Factor


:three: Convert Current → Pressure

Formula

Examples

Current (mA) Pressure (bar)
4 mA (4–4)×1.25 = 0 bar
8 mA (8–4)×1.25 = 5 bar
12 mA (12–4)×1.25 = 10 bar
16 mA (16–4)×1.25 = 15 bar
20 mA (20–4)×1.25 = 20 bar

:white_check_mark: Current Calculation When Pressure Range is Given (0–20 bar)

:one: Given

  • Pressure range = 0–20 bar

  • Current range = 4–20 mA


:two: Determine the Scaling Factor


:three: Convert Pressure → Current

Formula

Examples

Pressure (bar) Current (mA)
0 bar 4 mA
5 bar 8 mA
10 bar 12 mA
15 bar 16 mA
20 bar 20 mA

:warning: Note on Negative LRL

When the LRL is negative, always remember to subtract correctly:

Example:

  • LRL = −500 bar

  • URL = +500 bar

Total Span=URL−LRL=+500−(−500)=1000 bar

Negative ranges are very common in differential pressure measurement (vacuum to positive pressure).