Over current relays have a Standard Inverse operation (SI) [IEC 60255] with a ___

Over current relays have a Standard Inverse operation (SI) [IEC 60255] with a TMS setting of 0.5.

If using the CT Ratio 800/5 A and adjusting the current to 100% The fault current is equal to 5,000 A.

The relay’s tripping time is

A. 0.500 seconds
B. 1.875 seconds
C. 0.945 seconds
D. 3.750 seconds

Show Answer

Answer: B

Share your understanding of this question with the correct explanation.