Standard Inverse Overcurrent Relay connected to the current transformer ___

Standard Inverse Overcurrent Relay connected to the current transformer (CT) with Current Ratio of 1000/1 A, TMS = 0.1, adjusted to 125% if the current size of the fault occurs 5,000 A, relay operating time is

A. 0.1 seconds
B. 5.0 seconds
C. 0.5 seconds
D. 0.43 seconds

Show Answer

Answer: C

Share your understanding of this question with the correct explanation.