What is a major disadvantage of a 2-wire RTD connection?

What is a major disadvantage of a 2-wire RTD connection?

A. High power use
B. Slow response
C. Sensor noise
D. Lead wire error

View Answer

Answer: D

Explanation:

The biggest disadvantage of a 2-wire RTD connection is that the resistance of the lead wires is added directly to the RTD resistance, causing measurement errors.

The measuring instrument cannot distinguish between:

  • RTD resistance
  • Cable (lead wire) resistance

As a result, the displayed temperature is higher than the actual temperature.

For example:

  • Actual Pt100 resistance at 0°C = 100 Ω
  • Lead wire resistance = 2 Ω (1 Ω per wire)

Measured resistance:

100 Ω + 2 Ω = 102 Ω

The instrument interprets this extra resistance as additional temperature, creating an error.

Why the other options are incorrect:

  • High power use → RTDs use very little excitation current.
  • Slow response → Response time depends mainly on sensor construction and thermowell design.
  • Sensor noise → Not the primary disadvantage of a 2-wire RTD.
  • Lead wire error → The main limitation of 2-wire RTD measurements.

Because lead wire resistance directly affects the measurement, Option D (Lead wire error) is the correct answer. :white_check_mark: